Update: I quit running cat6 next to line voltage and my callbacks dropped to zero
Had a panel in Beaverton last month where the keypad kept dropping off the bus and I finally traced it to an ethernet run hugging a 120v romex for about 8 feet. Rerouted it in a separate chase and haven't had a single false alarm since, so yeah, I'm a believer now. What's your go-to separation rule, 6 inches or do you go further?